HRR and Temperature #14028
Unanswered
ShehabGamrah
asked this question in
Q&A
HRR and Temperature
#14028
Replies: 1 comment 2 replies
-
It is always a good idea to think about what kind of back of the napkin calculation can you do to estimate what you might expect from your simulation. Depending on what you have set for your REAC you will have a heat of combustion somewhere between 20 and 50 MJ/kg. So order of magnitude your 30 MW fire is 1 kg/s of fuel. Gas species have a specific heat around 1 kJ/kg. So every degree C above ambient that you set your burner will add about 1 kW of enthalpy to the domain. 300 C is going to add ~300 kW. Your fire size is 30,000 kW. What impact on temperature would you expect if you added 30,300 kW of heat vs. 30,000 kW of heat? |
Beta Was this translation helpful? Give feedback.
2 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
-
I have a question regarding HRR and temperature. I modeled a car park with an 8 MW fire and a 30 MW fire, but the resulting temperatures in both simulations were quite similar. I expected the temperature to increase significantly for the 30 MW fire. In both cases, the burner surface thermal temperature was set to 300°C. Does this setting control the temperature?
Beta Was this translation helpful? Give feedback.
All reactions